Ќе ги гледаш овие работи на Eurovent:
COP @ -7
Tbiv на колку и колкав COP@Tbiv (Бивалентна температура)
TOL и COP@TOL (Temperature Operation Limit - или (по дефиниција)
bivalent temperature
(Tbiv) means the outdoor temperature (Tj) [°C] declared by the manufacturer for heating at which the declared capacity equals the part load and below which the declared capacity must be supplemented with electric back up heater capacity in order to meet the part load for heating
operation limit temperature
(Tol) means the outdoor temperature [°C] declared by the manufacturer for heating, below which air conditioner will not be able to deliver any heating capacity. Below this temperature, the declared capacity is equal to zero
design load
means the declared cooling load (Pdesignc) and/or declared heating load (Pdesignh) [kW] at the reference design temperature, whereby for cooling mode, Pdesignc is equal to the declared capacity for cooling at Tj equal to Tdesignc for heating mode, Pdesignh is equal to the part load at Tj equal to Tdesignh
Кај браќава од кај најпрекрасните клими на светот со поштено наведени информации, што се тупаат в гради, TOL е -10 (минус десет, не минус 15 туку минус факинг десет)
Ама како сега ова, нели до -22 ги рекламираат и обичните поддржани со грејачи